Re: pool pump gfci
680.21 Motors.
(A) Wiring Methods.
(1) General. The branch circuits for pool-associated motors shall be installed in rigid metal conduit, intermediate metal conduit, rigid nonmetallic conduit, or Type MC cable listed for the location. Other wiring methods and materials
shall be permitted in specific locations or applications as covered in this section.
(4) One-Family Dwellings. In the interior of one-family dwellings, or in the interior of accessory buildings associated with a one-family dwelling, any of the wiring methods recognized in Chapter 3 of this Code shall be permitted that comply with the provisions of this paragraph. Where run in
a raceway, the equipment grounding conductor shall be insulated. Where run in a cable assembly, the equipment grounding conductor shall be permitted to be uninsulated, but it shall be enclosed within the outer sheath of the cable
assembly.
As per (A)(1), there are 4 permitted methods, UF not being one of them.
Notice how there is a statement " Other wiring methods and materials shall be permitted in
specific locations or applications as covered in this section.
Further in this section, (A)(4) permits for dwelling units
interior wiring to be any permitted chapter 3 method.
To answer your question of whether UF is permitted for outdoor installation to a permanent pool, I would say no.
As per .21(B), for double insulated motors, any chapter 3 method that is permitted for the location would be permitted. For this type of motor I would say yes to UF cable. But don't forget about the last sentence in this section. If you have that situation, then a raceway will be required. (
the last sentence is in the '05 NEC, it is not in the '02 version )
Isn't this fun
[ May 04, 2005, 11:51 PM: Message edited by: pierre ]