pool pump GFI

Status
Not open for further replies.

jwelectric

Senior Member
Location
North Carolina
Re: pool pump GFI

680.12 Maintenance Disconnecting Means.
One or more means to disconnect all ungrounded conductors shall be provided for all utilization equipment other than lighting. Each means shall be readily accessible and within sight from its equipment.

680.21 Motors.
(A) Wiring Methods.
(1) General. The branch circuits for pool-associated motors shall be installed in rigid metal conduit, intermediate metal conduit, rigid nonmetallic conduit, or Type MC cable listed for the location. Other wiring methods and materials shall be permitted in specific locations or applications as covered in this section. Any wiring method employed shall contain an insulated copper equipment grounding conductor sized in accordance with 250.122 but not smaller than 12 AWG.

hope this helps
:)
 

benaround

Senior Member
Location
Arizona
Re: pool pump GFI

JW,

This is a little off the track,If elec5555 installs a fused disconnect for the pump,will that make the supply to the disc. FEEDERS and the rest branch circuit conductors?
 

jwelectric

Senior Member
Location
North Carolina
Re: pool pump GFI

680.25 Feeders.
(A) Wiring Methods. Feeders shall be installed in rigid metal conduit, intermediate metal conduit, liquidtight, flexible nonmetallic conduit, or rigid nonmetallic conduit. Electrical metallic tubing shall be permitted where installed on or within a building, and electrical nonmetallic tubing shall be permitted where installed within a building.

(B) Grounding. An equipment grounding conductor shall be installed with the feeder conductors between the grounding terminal of the pool equipment panelboard and the grounding terminal of the????.. this equipment grounding conductor shall be insulated.

(1) Size. This conductor shall be sized in accordance with 250.122 but not smaller than 12 AWG.
Does this help with understanding how to install feeders?
Notice that when we install feeders we now have to run the conductors in pipe all the way to the service.
We would be better off installing a no fuse at the pool.
 

benaround

Senior Member
Location
Arizona
Re: pool pump GFI

JW,

The question popped into my head while reading OP's question,it stemmed from the A/C debate I'm sure you know what I'm talkink about.

Thank You, for your reply. For that matter,thanks for your many interesting,informative,and never boring replys
 