Jimmy7
Senior Member
- Location
- Boston, MA
- Occupation
- Electrician
I have a customer who has asked me to wire his replacement pool pump. The pool pump is 115 volt, 15 Amp, 1 HP. I was going to feed the pump with a 20 Amp single pole gfci breaker. There is currently a 1/2" pvc conduit from the electrical panel to where the original pump was located. This conduit contains the feed for the pool light as well. The distance from the electrical panel to the pump location is approximately 60'. As a result, I was going to use #10 for the pump due to voltage drop. Is this correct? I was then thinking I would have to increase the size of the grounding conductor as well.
Does the ground wire need to be #8?
#10 (10380) / #12 (6530) = 1.59
250.122 - 20A = #12 #12 6530 Circ Mils 6530 x 1.59 = 10382
Can I use a #10 that is 10380 Circ Mils, or do I have to go up to #8 16510 Circ Mils?
If I go to a #8 will it fit in the with the existing conductors in the 1/2" conduit?
Does the ground wire need to be #8?
#10 (10380) / #12 (6530) = 1.59
250.122 - 20A = #12 #12 6530 Circ Mils 6530 x 1.59 = 10382
Can I use a #10 that is 10380 Circ Mils, or do I have to go up to #8 16510 Circ Mils?
If I go to a #8 will it fit in the with the existing conductors in the 1/2" conduit?