brantmacga said:
oh really???
Nec 2008 680.22(B) GFCI Protection. Outlets supplying pool pump motors from branch circuits with short-circuit and ground-fault protection rated 15 or 20 amperes, 125 volt or 240 volt, single phase, whether by receptacle or direct connection, shall be provided with ground-fault circuit-interrupter protection for personnel.
That's a new section

Read 680.22 (5) in the 2005
 
stickboy1375 said:
Hey, I dont know much, but I know if I ever invent something, I sure want it to be code to use as much as possible of it! :grin:

That's the quickest way to making millions!
 