Pool room enclosure with panel inside

Status
Not open for further replies.
I am working with a retirement facility currently nearing end of construction. Pool s up and running but not turned over yet. I am compiling a list of issues with pool equipment and one of them is a breaker box located inside the enclosed room with no stainless steel enclosure to protect from moisture.

What is NEC code for panel board located inside wet environments? There is a drainage line on the floor. Is a waterproof case required or simply suggested?

thanks for your time
 
Is this room expected to be wet with any regularity? Occasional leakage when disconnecting plumbing for maintenance or repairs doesn't necessarily make it a wet location. If the room is regularly washed down that could make it a wet location.

Stainless is not required for wet locations either. It is a good option when there is corrosive agents in the area though.
 