busman
Senior Member
- Location
- Northern Virginia
- Occupation
- Master Electrician / Electrical Engineer
The situation is this; I have a hot tub (spa) that was wired by a pool company. The feeder to the spa panel is within 5 feet of the wall of the spa and so is the panel itself.
The question is, does this violate the code? I think we would all say it violates the intent of the code, but the only thing I could find was 680.10 (2005 NEC) that says wiring can't be within 5 feet, unless it is necessary to supply pool equipment. In my mind this could be read two ways:
1) Wiring is prohibited within 5 feet if it's not associated with the pool. For instance, I can't run a feeder out to a shed and pass it under the pool.
or
2) Wiring is prohibited within 5 feet unless there is no other way. For instance wiring to an in-pool light obviously MUST go into the 5 foot zone to get to the light. But, if in the case of the panel and feeder, they CAN be routed outside the zone, so they MUST be routed outside the zone.
Am I missing something? Also if #1 is the correct interpretation, then I can put the pool panel within 5 feet of the pool? I didn't see an article that specifically mentions panels.
Thanks,
Mark
PS: Does 680.6 really require me to ground a non-metallic junction box? It seems to say so.
The question is, does this violate the code? I think we would all say it violates the intent of the code, but the only thing I could find was 680.10 (2005 NEC) that says wiring can't be within 5 feet, unless it is necessary to supply pool equipment. In my mind this could be read two ways:
1) Wiring is prohibited within 5 feet if it's not associated with the pool. For instance, I can't run a feeder out to a shed and pass it under the pool.
or
2) Wiring is prohibited within 5 feet unless there is no other way. For instance wiring to an in-pool light obviously MUST go into the 5 foot zone to get to the light. But, if in the case of the panel and feeder, they CAN be routed outside the zone, so they MUST be routed outside the zone.
Am I missing something? Also if #1 is the correct interpretation, then I can put the pool panel within 5 feet of the pool? I didn't see an article that specifically mentions panels.
Thanks,
Mark
PS: Does 680.6 really require me to ground a non-metallic junction box? It seems to say so.