For the first time I am doing a pool wiring.
So, my understanding is:
I could not figure out if the pool panel (when sized properly) can supply A/C circuit that is next to the pool equipment?
Thank you.
- based on 680.25(A)(1) I must use the wiring method that is mentioned in the article for the supply side feeder and I can not use NM cable to supply the panel of the pool equipment. And it must have a insulated EGC from the pool panel straight to the service panel.
- It seems like SCH80 PVC will do just fine for the branch circuits that are for the pumps and the pool lighting.
- Pool lights, receptacles, pool pumps all to be GFCI protected.
- The bonding grid conductor minimum #8 solid copper will bond the rebar, lighting shell, motor frames, he ladder, the diving board, the 36" perimeter walkway rebar....
Thank you.