pool wiring burial depths

Status
Not open for further replies.

inspector23

Senior Member
Location
Temecula, CA
I am looking for clarification of 2002 NEC Article 680.10 - (Underground Wiring Locations), on page 526.

The article states " Underground wiring shall not be permitted under the pool or within the area extending 1.5 m (5ft.) horizontally from the inside wall of the pool unless this wiring is necessary to supply pool equipment permitted by this article. Where space limitations prevent wiring from being routed a distance 1.5 m (5ft) or more from the pool. such wiring shall be permitted where installed in rigid metal conduit, intermediate metal conduit, or a nonmetallic raceway system. All metal conduit shall be corrosion resistant and suitable for the location. The minimum burial depth shall be as given in table 680.10."

The table 680.10 lists nonmetallic raceways listed for direct burial without concrete encasement as 18 inches.

My questions are:

1. What is the NEC definition of encasement? I did not find it in either the general definitions or those definitions specifically for Article 680. Does laying in the bottom of the trench, getting covered in concrete, constitute "encasement"?

2. If you do indeed consider this "encasement", then what is the correct burial depth for the nonmetallic raceway? It is not listed in Table 680.10

3. Why 18 inches for nonmetallic ? If the trench area is getting filled and a 4" slab of concrete poured over it, why is that not sufficient protection for the raceway?

4. If the wiring is not specifically used for the pool equipment, I interpret the article to say the conduit is not allowed if it can indeed be placed further than 5 ft from the inside edge of the pool. Is that a correct assessment?

Any enlightenment be greatly appreciated.
 
Re: pool wiring burial depths

Thanks for the quick response, but where did you get your definition for # 1? It is not listed in the NEC that I can find, and there is not specific number of inches I can find under the general word "encasement" in Webster's dictionary. Just wondering......

I am also having difficulty with Number 3 answer ( to see table 300.5).

It does not seem to work if you follow 680.10. If you have a nonmetallic raceway listed for direct burial without concrete encasement (680.10), the minimum depth is 18". Table 300.5 says you can go as shallow as 4" if you place it under a minimum of 4" of concrete. I guess I am just not getting it. Referring me to table 300.5 is not telling me WHY I need 18" if within 5' of the pool edge. In fact, since it is less restrictive that 680.10, it places a spotlight upon WHY does it need to be 18".

What is the intent?

Thanks again for your help...
 