Back in the day they used to be very common. The code still recognizes them but I haven't seen one installed for at least 40-50 years. I wold not have one. I'm not sure if you can even still buy one. Sort of like copper clad AL building wire-it is code recognized but not made by anybody anymore.So, I must keep any 120v wiring, like for landscape lighting for instance at least 5' away from pool, but I can have a 120v light IN the pool? What is up with that???
Within 5’ has to basically be in conduit 680.11 (2020 NEC)Wasn't the 5' rule for underground wiring removed in the 2017 NEC?
2017 NEC:
680.11 Underground Wiring Location. Underground wiring shall be permitted where installed in rigid metal conduit, inter‐
mediate metal conduit, rigid polyvinyl chloride conduit, reinforced thermosetting resin conduit, or Type MC cable, suitable
for the conditions subject to that location. Underground wiring shall not be permitted under the pool unless this wiring is
necessary to supply pool equipment permitted by this article. Minimum cover depths shall be as given in Table 300.5 .
2014 NEC:
680.10 Underground Wiring Location. Underground wiring shall not be permitted under the pool or within the
area extending 1.5 m (5 ft) horizontally from the inside wall of the pool unless this wiring is necessary to supply
pool equipment permitted by this article. Where space limitations prevent wiring from being routed a distance 1.5 m
(5 ft) or more from the pool, such wiring shall be permitted where installed in complete raceway systems of rigid metal
conduit, intermediate metal conduit, or a nonmetallic raceway system. All metal conduit shall be corrosion resistant
and suitable for the location. The minimum cover depth shall be as given in Table 680.10.