shortcircuit2
- South of Bawstin
My buddy's portable room AC unit is tripping the 15-amp breaker so he asked me to take a look. He has 2 of the exact same standup room 120-volt plug in AC units that nameplate draw 10.2 amps. 1 unit on a 1st floor 20-amp circuit and 1 unit in a 2nd floor bedroom on a 15-amp circuit. The 2nd floor unit trips the 15-amp breaker in about first 2-minutes of operation.
20-amp branch circuit AC drawing 12.4 amps and 15-amp AC drawing 14.8 amps...
Swapped 15-amp breaker with new 15-amp and same thing happens...
Then we tried switching AC units...but same thing happened...
Now I am thinking voltage drop on 15-amp branch circuit due to loose connections or back stabbed receptacles. Nope, all connections are tight with wrap around screw connections...
There is 103-volts to ground at the branch breaker, main breaker and at the weather head...
The nameplate on the AC unit(s) says minimum 103-volts...
So i throw my amprobe on the wire at the 15-amp breaker and watch the amps rise from 12-amps all the way to 30-amps which trips the breaker...
During another test, I watch the voltage drop to 98-volts just before the breaker trips.
So my conclusion is that the 103-volts coming in from the Utility transformer is the root of the problem. It is only causing the problem on the 15-amp branch circuit. The 20-amp circuit holds at just under 13-amps. There are 6-houses all running their AC on a wicked humid day on 1 pole mounted 25kva transformer.
I may go back today to see if the voltage is any higher. It is much cooler today.