625.44 Equipment Connection
EVSE and WPTE shall be connected to the premises wiring system in accordance with one of the methods in 625.44(A) through (C).
(A) Portable Equipment
Portable equipment shall be connected to the premises wiring system by one or more of the following methods:
A nonlocking, 2-pole, 3-wire grounding-type receptacle outlet rated at 125 volts, single phase, 15 or 20 amperes
A nonlocking, 2-pole, 3-wire grounding-type receptacle outlet rated at 250 volts, single phase, 15 or 20 amperes
A nonlocking, 2-pole, 3-wire or 3-pole, 4-wire grounding-type receptacle outlet rated at 250 volts, single phase, 30 or 50 amperes, or 125/250 volts, single-phase, 30, 50, or 60 amperes
A nonlocking, 2-pole, 3-wire grounding-type receptacle outlet rated at 60 volts dc maximum, 15 or 20 amperes
(B) Fastened-in-Place Equipment
Equipment that is fastened-in-place shall be connected to the premises wiring system by one of the following methods:
A nonlocking, 2-pole, 3-wire grounding-type receptacle outlet rated 125 volts or 250 volts, single phase, up to 50 amperes
A nonlocking, 3-pole, 4-wire grounding-type receptacle outlet rated 250 volts, three phase, up to 50 amperes
A nonlocking, 3-pole, 4-wire grounding-type receptacle outlet rated 125/250 volts, single phase, 30, 50, or 60 amperes
A nonlocking, 2-pole, 3-wire grounding-type receptacle outlet rated 60 volts dc maximum, 15 or 20 amperes
(C) Fixed-in-Place Equipment
All other EVSE and WPTE shall be permanently wired and fixed-in-place to the supporting surface.