I want to hook a 7500w/9500peak generator to my service panel. The gas generator will be outside.
My method GE interlock kit.
Nameplate 240v 31 amp
Wire 31x1.15=35.65 #8 copper
Breaker 30amp 2 pole
My confusion
my thought was to disconnect the bonding jumper at the generator being as I will not switch the neutral. Is this correct?
But the generator will be outside. I have myself confused between 250.30-250.34.
The generator does have a mounted disconnect. I was going to hook up to the L14-30R receptacle on the generator please see picture
My method GE interlock kit.
Nameplate 240v 31 amp
Wire 31x1.15=35.65 #8 copper
Breaker 30amp 2 pole
My confusion
my thought was to disconnect the bonding jumper at the generator being as I will not switch the neutral. Is this correct?
But the generator will be outside. I have myself confused between 250.30-250.34.
The generator does have a mounted disconnect. I was going to hook up to the L14-30R receptacle on the generator please see picture