If a portable generator is used as a "stand by" generator for a residential house, does the neutral have to be separated in the generator? I couldn't find it in the Code reference. Thanks
I removed the neutral bond from my generator since I'm operating as a non-SDS. Very easy task took less than 10 minutes.The problem is that the generator manual says to put on GFCI protection if operated in any damp area, and it will be located outside of course.
So I guess that would answer my question that they should be separated. Thanks
Does the removal of that connection result in voiding of any warranties or failure to follow any manufacturer's recommendations ? Also, did you drive a ground rod ? You know the EI that I'm dealing with up here.I removed the neutral bond from my generator since I'm operating as a non-SDS. Very easy task took less than 10 minutes.
I remember at least one manufacturers instructions (don't remember which one I think it was Honda) telling the user to make the change and showing how to do it.Does the removal of that connection result in voiding of any warranties or failure to follow any manufacturer's recommendations ? Also, did you drive a ground rod ? You know the EI that I'm dealing with up here.
It likely voids the warranty but I know that on my Generac it can be reinstalled just as easily as it is removed. A ground rod is not required if the neutral is not switched.Does the removal of that connection result in voiding of any warranties or failure to follow any manufacturer's recommendations ? Also, did you drive a ground rod ? You know the EI that I'm dealing with up here.
I'm with you BUT, you know what I'm dealing with up here. It clearly states on page 27 of the instruction manual to "ground the generator to a ground rod or risk the possibility of electrocution." That's all this EI needs to see to fail this installation. I can hardly wait to see what other BS he finds.It likely voids the warranty but I know that on my Generac it can be reinstalled just as easily as it is removed. A ground rod is not required if the neutral is not switched.
Yes somewhere I have that instruction from Honda. I may be able to post it laterI remember at least one manufacturers instructions (don't remember which one I think it was Honda) telling the user to make the change and showing how to do it.
I'm with you BUT, you know what I'm dealing with up here. It clearly states on page 27 of the instruction manual to "ground the generator to a ground rod or risk the possibility of electrocution." That's all this EI needs to see to fail this installation. I can hardly wait to see what other BS he finds.
This unit will never be used at a remote site. There's no need to do a continuity check from N-G. The schematic in the instruction manual clearly shows a bond between the two. I will have to remove that jumper.Most installation instructions have the statement : "Install according to local codes" or similar. The NEC is adopted in most juridictions and a ground rod is not required if a portable genset is connected to a homes electrical system with a bond at the service disconnect.
To check if a generator is bonded, do a continuity test between the ground and neutral of the receptacle on the genset (while it is off of course). It is "bonded" with continuity between gound and neutral.
It should be an unbonded genset (floating neutral) if connected to a homes electrical system which has a "bond" at the service.
But if you want to use that same portable generator at say a campsite or jobsite, the ground and neutral should be tied at the genset.
Good info and smart thinking.I use a male cordcap with a jumper between ground and neutral to make the "bond" by inserting the cordcap into a receptacle on the genset when I use my homes portable (unbonded) backup generator at a jobsite.
How else can you keep neutral current off of the EGC? The sub-panel feeder comparison is valid.I'm missing the direct one that says they must be separated. I'm looking in the 2017 code. I see of course where the generator has to be grounded, but am failing to see where the neutral cannot be connected to it, unless we go back to treating it as a "sub panel" sort of thing.
End of story.He said "leave the jumper in place and remove the wire to the ground rod."