Funny how the simplest things can stump you sometimes...
We have a generator we need to hook up to a panel to power some construction trailers. We'll be hooking up at 120/208V 3ph, and the generator is rated for 78kVA at this voltage (~216A). I'd like to hook it up to a 225A panel, w/ a 225A main breaker. The thing is, the generator has a 400A 3P breaker on it where we intend to hook up... do I need to size the conductor to 400A?
I'm thinking we can size to 225A based on the main breaker of the panel, but I'm just not totally sure. This is in Canada btw, but if there's an NEC clause that'd be helpful as well.
Thanks,
Mike
We have a generator we need to hook up to a panel to power some construction trailers. We'll be hooking up at 120/208V 3ph, and the generator is rated for 78kVA at this voltage (~216A). I'd like to hook it up to a 225A panel, w/ a 225A main breaker. The thing is, the generator has a 400A 3P breaker on it where we intend to hook up... do I need to size the conductor to 400A?