goldstar
Senior Member
- Location
- New Jersey
- Occupation
- Electrical Contractor
I recently installed one of those Reliance 10 circuit manual generator transfer switches with a remote 30A, 120/240V plug-in port (all customer purchased material including the Honda generator & cord). Everything went smooth and interfaced it into a main breaker panel with considerable ease. However, I was not able to test the operation with the generator for a number of reasons, all of which were the HO's problem.
As luck would have it, there was a power failure while I was away on vacation and I got a call from the HO stating that as soon as he plugged the cord into the genaretor and then the remote port (before transferring any circuits) the breaker on the generator tripped immediately. So, I went out today and discovered that ALL the receptacles on this particular generator were GFCI protected via the portable generator distribution panel, including the 30A, 120/240 receptacle.
My immediate solution was to disconnect the green ground wire between the xfer switch panel and the main breaker panel but the 1 1/4" greenfield connecting between the two panels provided a redundant ground path. So, I disconnected the greenfield from the xfer panel and allowed it to float.
So, now what I have is a properly grounded main breaker panel but the xfer panel is not bonded in any way to the MB panel and does not have a common ground path. The xfer panel will be bonded to the grounded casing of the generator during a power fail condition (with the cord attached) and will be providing power to the 10 circuits in the house without a common ground path to the MB panel in a power fail condition.
Any suggestions on how you would properly correct this would be appreciated. I'm thinking I'm either screwed or I should let the xfer panel float and not worry about it. BTW, until now I've never come across a portable generator that has a GFI protected 120/240V output.
I probably could pull the generator distribution board off and re-wire the 120/240V circuit so it's not GFI protected. I'm not concerned about voiding any warranties at this point. I just want to do this the safest way.
Thanks in advance.
Phil,
Gold Star Electric
New Jersey
As luck would have it, there was a power failure while I was away on vacation and I got a call from the HO stating that as soon as he plugged the cord into the genaretor and then the remote port (before transferring any circuits) the breaker on the generator tripped immediately. So, I went out today and discovered that ALL the receptacles on this particular generator were GFCI protected via the portable generator distribution panel, including the 30A, 120/240 receptacle.
My immediate solution was to disconnect the green ground wire between the xfer switch panel and the main breaker panel but the 1 1/4" greenfield connecting between the two panels provided a redundant ground path. So, I disconnected the greenfield from the xfer panel and allowed it to float.
So, now what I have is a properly grounded main breaker panel but the xfer panel is not bonded in any way to the MB panel and does not have a common ground path. The xfer panel will be bonded to the grounded casing of the generator during a power fail condition (with the cord attached) and will be providing power to the 10 circuits in the house without a common ground path to the MB panel in a power fail condition.
Any suggestions on how you would properly correct this would be appreciated. I'm thinking I'm either screwed or I should let the xfer panel float and not worry about it. BTW, until now I've never come across a portable generator that has a GFI protected 120/240V output.
I probably could pull the generator distribution board off and re-wire the 120/240V circuit so it's not GFI protected. I'm not concerned about voiding any warranties at this point. I just want to do this the safest way.
Thanks in advance.
Phil,
Gold Star Electric
New Jersey
Last edited: