Portable generator

Malywr

Senior Member
Location
New Jersey USA
Can i use existing dryer line 10/2 for inlet portable generator ?
Do i need to run new cable 10/3 across entire house?
Panel is in garage and customer wants generator located on backyard. He is not using dryer receptacle anymore.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
Can i use existing dryer line 10/2 for inlet portable generator ?
Do i need to run new cable 10/3 across entire house?
Panel is in garage and customer wants generator located on backyard. He is not using dryer receptacle anymore.
No, and yes.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
Do you mean I can not use dryer circuit 10/2?
First question -No
Second question - Yes
Exactamundo.

First (unless you only have a 120v genny), you shouldn't use the bare EGC as the neutral.

Second, yes, you need a 4-wire feeder that does not land on a non-interlocked breaker.
 