Portable Generator

Status
Not open for further replies.

GSXR600

Senior Member
The general contractor is bringing a portable generator to our job site. Dont you have to drive a ground rod and bond the building steel?
 
What does it say i dont have my code book handy

................

250.34 Portable and Vehicle-Mounted Generators.
(A) Portable Generators. The frame of a portable generator shall not be required to be connected to a grounding electrode as defined in 250.52 for a system supplied by the generator under the following conditions:
(1) The generator supplies only equipment mounted on the generator, cord-and-plug-connected equipment through receptacles mounted on the generator, or both, and
(2) The normally non?current-carrying metal parts of equipment and the equipment grounding conductor terminals of the receptacles are connected to the generator frame.
 