I am looking for some advice on a job that has recently came my way.
The local volunteer fire dept. has requested that I install a transfer switch for a portable generator. They have a 55kW, trailer-mounted, diesel generator that they want to use to power the station during power outages. The station is currently powered through a 200A main panel.
I understand the transfer switch portion of the equation, but I am struggling with conductor sizing (for generator connection leads).
I am afraid my calulations are off for the current-carrying conductors. According to the 2002 NEC, I am interpreting that these must be sized to handle 263A, which means 300kcmil @ 75C. Is this correct or have I messed up? Also, I am seeing the neutral as having to be sized for 140A, which means 1/0 @ 75C. At that point, I got frustrated and decided to put the questions to the experts. Could you please point me in the right direction?
P.S. What about grounding? Do I need to tie the generator, when in service, to the building ground, or drive a separate ground rod?
Thanks in advance for all the help. I haven't installed a setup like this before.
Harvey828
The local volunteer fire dept. has requested that I install a transfer switch for a portable generator. They have a 55kW, trailer-mounted, diesel generator that they want to use to power the station during power outages. The station is currently powered through a 200A main panel.
I understand the transfer switch portion of the equation, but I am struggling with conductor sizing (for generator connection leads).
I am afraid my calulations are off for the current-carrying conductors. According to the 2002 NEC, I am interpreting that these must be sized to handle 263A, which means 300kcmil @ 75C. Is this correct or have I messed up? Also, I am seeing the neutral as having to be sized for 140A, which means 1/0 @ 75C. At that point, I got frustrated and decided to put the questions to the experts. Could you please point me in the right direction?
P.S. What about grounding? Do I need to tie the generator, when in service, to the building ground, or drive a separate ground rod?
Thanks in advance for all the help. I haven't installed a setup like this before.