The more I am reading the more I am confusing myself.
We have a residence with a "generator" panel fed thru a 2PDT manual transfer switch.
250.24 requires there be no grounded-grounding connection on the load side of my service
disconnect so the T/S has an isolated neutral and in this case, unswitched.
The customer is going to rely on a portable generator which is not on site.
Connection will be made thru a permanently installed "inlet" via a cord & plug to the generator.
All of the 50 amp generator inlets I have found are 240/120 3 wire which would not allow for an equipment grounding conductor to the generator.
On a permanent generator install, if we the T/S switch did not switch the neutral, we would need the equipment grounding conductor to the generator. Are portable generators handled differently ?