portable genset OCPD
I've got a Coleman Powermate 5/6.25KW portable generator with 25A breakers. Can i go up to 30A without doing any damage? I know it's pointless to try and ask Coleman.
If your 30A breakers are after your 25A breaker, the 25A will (most likely) trip before the 30A.
If you're asking if you can change the 25A to 30A, then I guess it really depends on your skills. Physically you probably can, but is it code compliant? Probably not. Will it work? Maybe for a little while ... you may start to pull your frequency or voltage down though.
I doubt that merely changing the breaker to 30A would do any damage. But running it at a higher current level probably would over time. The breaker is partially there to protect the generator from running with too high of a load.
I'd be replacing the Coleman factory breakers on the unit itself with the next size up. Then my transfer switch will have a 30A breaker in it. Constant load will not be a full 30 amps, but might be more than 25amps. I just want to know if the generator can handle UP TO to 30 amps.
Problaby not. I would guess the 5/6.25 means the generator is rated at 5000 watts (5KW) and 6250 VA's (6.25KVA).
That's a maximum of 26 amps at 240 volts.
You mean Powermate 5000 Watt (constant) 6250 Watt (peak power) generator? Or the 6250 Watt (constant) model? Whichever- What matters is CONSTANT/ CONTINUOUS output rating. That's what it can run safely at (safely means not self destructing).
PEAK output is only for non-continuous motor starting surges (frige, oil burner,etc), short bursts of higher output,. Try running it at the PEAK rating for a longer time, you'll fry it (probably pretty quick).
I wouldn't change built-in breakers to higher amps unless generator was free and you have another to replace it with when it burns up.