Portable heater

Status
Not open for further replies.

Chayvo

Member
Location
Kazakhstan
I have a portable Chinook air heater which can either powered by mains power or via the onboard generator.When powered by mains 480V I have a 4 conductor cable 3phases plus a ground conductor which serves as a ground back to the MCC.Do I need to install a ground rod as well?Looking at NEC 250.34 they way I read it you dont if run on generator power, so what would the difference be if running off mains power?Any ideas on this welcombe.
 

tom baker

First Chief Moderator
Staff member
No purpose for a ground rod at the heater. It won't clear a fault.
We need to know more about the generator.
Is the neutral switched in the transfer switch?
 