Cow
Senior Member
- Location
- Eastern Oregon
- Occupation
- Electrician
I'm getting ready to quote wiring a portable job trailer like you see on any typical jobsite, in a jurisdiction known to have inspectors that are sticklers. So I want to cover my bases.
I'll admit, this is the first time I've looked up codes on job trailers for as long as I can remember.:ashamed1:
My main two questions relate to feeder size and installing a GES.
1. Reading 550.4(A) leads me to believe article 550 applies. (I've searched, it's seems this article and 545 have been debated a fair amount). To paraphrase part of 550.4(A), "shall not be required to meet the provisions of this article pertaining to the number or capacity of circuits required." Then on to 550.33(B) which mentions "feeder circuit conductors....shall be rated not less than 100 amperes."
So, am I able run #2 AL to this trailer with a 60-90 amp breaker as long as it meets the calculated load of the trailer since 550.4(A) seems to give me a pass on the 100 amp minimum?
2. When I install the rods, am I allowed to attach the GEC to the steel trailer frame which is typically bonded with a #6 green back to the panel from the factory or must I fish the GEC up into the interior panelboard?
Thanks.
It's one of those things I think, where the older I get, the less I know, or remember. Maybe I said that wrong, I don't remember how it goes...
I'll admit, this is the first time I've looked up codes on job trailers for as long as I can remember.:ashamed1:
My main two questions relate to feeder size and installing a GES.
1. Reading 550.4(A) leads me to believe article 550 applies. (I've searched, it's seems this article and 545 have been debated a fair amount). To paraphrase part of 550.4(A), "shall not be required to meet the provisions of this article pertaining to the number or capacity of circuits required." Then on to 550.33(B) which mentions "feeder circuit conductors....shall be rated not less than 100 amperes."
So, am I able run #2 AL to this trailer with a 60-90 amp breaker as long as it meets the calculated load of the trailer since 550.4(A) seems to give me a pass on the 100 amp minimum?
2. When I install the rods, am I allowed to attach the GEC to the steel trailer frame which is typically bonded with a #6 green back to the panel from the factory or must I fish the GEC up into the interior panelboard?
Thanks.
It's one of those things I think, where the older I get, the less I know, or remember. Maybe I said that wrong, I don't remember how it goes...