Have a big gen set with a 2500amp main that is feeding 3 VFD’s.
I’m not responsible for load side of vfd to the pump but only supplying power with portable power cable that has already been supplied from the general contractor and rental company. Type W, TF CABLE. Size 4/0 with ampacity of 405amperes.
Running parallels 2 conductors per phase will terminate in a 800amp breaker in the vfd.
I know I have to size my EGC from the source breaker feeding (2500amp) which would be a 350mcm.
My only question is since this type of cable has a higher ampacity than typical do I still size per 250.122?
I know grounding conductors need not be larger than phase conductors so I was just going to install two 4/0 for my EGC as well.
I am just wondering if it was still sized per 250.122 which I believe it should be.