Portable Power Cables Section 555.13 (Connection between Land and Floating Dock)

Status
Not open for further replies.

kmass

Member
Location
Long Island
Occupation
Engineer
Our project involves re-wiring electric to power posts located on a floating dock system. The 600 Amp electric sub-panels (NEMA 4x enclosures) will be located on-land directly adjacent to the gangways leading to the floating docks. Do these sub-panels with NEMA 4X enclosures meet the requirements of section 555.13(B)(4) Portable Power Cables or is another type of junction box with terminal blocks required?
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
We may be overlooking or mis-reading but locally the panels on shore are NEMA 3R
 

kmass

Member
Location
Long Island
Occupation
Engineer
Assuming the Panels are NEMA 3R would this be an acceptable method of wiring? In other words connect the portable power cables directly to the panel and then out to the floats? Or is some sort of intermediate junction box with terminal blocks required.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Our guys normally sleeve the cable in conduit to the shore panel and use pin sleeves to terminate.
 