I am looking for clarification on the use of single conductor 4/0 AWG DLO Portable Power Cable Type W in a industrial recycle crushing application. 150hp 3 phase induction motor wired to properly sized motor starter,overload,short circuit, and disconnecting means. The plant is a portable plant that moves approximately every 6 months or less. All equipment is on tractor trailers and the plant is powered by 600kw generator (no utility power). All motors are wired using multi conductor power cables. However, the large crusher motors are using individual portable power cables per phase plus seperate conductor for ground. Cords are hard wired at starter and the motor has a junction box with bulk head fittings. Cord bodies and bulk head fittings are UL listed and rated at 405 amperes, however, they do not have a hp rating and the small writing on the paperwork says not for use on motor loads. Contacted the manufactuer and was told that they are not rated to make and break motor loads, but if wired to proper motor starter as per NEC that this was a legal application. Customers are really happy with this type of hook up, but we are wanting to make sure we are within NEC code. I would appreciate any input on how to get a proper answer.