I have a situation where a heat treatment machine requiring a 125A, 480V 3-phase supply is being installed. The machine will be moved around frequently to accommodate other equipment in the area (a weld shop), so the thought is to run type W flexible power cable from a wall mounted disconnect to the machine, a distance of not more than 15 feet. The source will be a nearby panelboard with space for a 125A3P breaker. The circuit from the panel to the disconnect will be regular THHN conductors in GRC. The flexible cable will be protected in accordance with 400.13 and 240.5.
The one area causing me some concern is whether or not type W cable, or any flex cable for that matter, is suitable for termination to a permanently installed disconnect. For those who may wonder, I had considered the installation of a 125A 480V receptacle, but the models I've found have been rated for European voltages. Thanks for any input.
The one area causing me some concern is whether or not type W cable, or any flex cable for that matter, is suitable for termination to a permanently installed disconnect. For those who may wonder, I had considered the installation of a 125A 480V receptacle, but the models I've found have been rated for European voltages. Thanks for any input.