BUMP....was hoping to get some thoughts on this.....
Is this what you are looking for?
430.42(C) Cord-and-Plug-Connected. Where a motor is connected
to a branch circuit by means of an attachment plug and
a receptacle or a cord connector, and individual overload protection
is omitted as provided in 430.42(A), the rating of the
attachment plug and receptacle or cord connector shall not
exceed 15 amperes at 125 volts or 250 volts. Where individual
overload protection is required as provided in 430.42(B) for a
motor or motor-operated appliance that is attached to the
branch circuit through an attachment plug and a receptacle or
a cord connector, the overload device shall be an integral part
of the motor or of the appliance.
The rating of the attachment
plug and receptacle or the cord connector shall determine the
rating of the circuit to which the motor may be connected, as
provided in 210.21(B).