I am trying to understand something here.
410.151(A) requires permanent connection of track lighting to a branch circuit. So does this exist?
I don't see how this exists, or why 410.151(A) has been in the code so many years if you can buy a "portable electric luminaire" that is a track light. :?
410.151(A) requires permanent connection of track lighting to a branch circuit. So does this exist?
The Author of My Book said:
Portable lighting tracks, per UL Standard 153 shall
? not be longer than 8 ft (2.4 m).
? have a cord not less than 5 ft (1.5 m) permanently attached to the track by the manufacturer.
? have overcurrent protection (fuse or circuit breaker) built into the plug cap. Overcurrent protection in the plug cap is not required if the conductors in the cord are 12 AWG, rated 20 amperes.
? not have its length altered in the field. To do so would void the UL listing.
I don't see how this exists, or why 410.151(A) has been in the code so many years if you can buy a "portable electric luminaire" that is a track light. :?