We're having a problem with electrical interference on a fire alarm system.
We have a Fire Alarm Control Panel installed in a building, where the conduit is run underground to a concrete pad that's elevated above grade about 4', on concrete pillars. On the pad, we've got a stainless steel junction box that's not painted, and is mounted on galvanized, unpainted steel columns.
When we meter from the steel structure to earth surrounding the columns, we're seeing about 0.6 Volts DC. When the circuit is installed in the conduit, it causes problems with the FACP. Outside of the conduit it's fine. The conduit is fastened to the galvanized steel structure very well. In looking at the structure however we don't see any bonding straps on the steel, or any connections to a ground rod.
The electrical engineer advised that they have cathodic protection in the plant with 12 VDC. I believe that because the steel on the pad is not properly grounded and that's what's giving us fits.
A conduit for the light fixture comes up from the ground, out of a trench, and i'm told some portion of this rigid conduit is in contact with earth before it comes in contact with the pad. I haven't see where the cathodic protection is installed, if at all on this pad (outdoor pad), but if it is being used there, I can't see how it would work if there's no return path to earth.
Can someone enlighten me?
We have a Fire Alarm Control Panel installed in a building, where the conduit is run underground to a concrete pad that's elevated above grade about 4', on concrete pillars. On the pad, we've got a stainless steel junction box that's not painted, and is mounted on galvanized, unpainted steel columns.
When we meter from the steel structure to earth surrounding the columns, we're seeing about 0.6 Volts DC. When the circuit is installed in the conduit, it causes problems with the FACP. Outside of the conduit it's fine. The conduit is fastened to the galvanized steel structure very well. In looking at the structure however we don't see any bonding straps on the steel, or any connections to a ground rod.
The electrical engineer advised that they have cathodic protection in the plant with 12 VDC. I believe that because the steel on the pad is not properly grounded and that's what's giving us fits.
A conduit for the light fixture comes up from the ground, out of a trench, and i'm told some portion of this rigid conduit is in contact with earth before it comes in contact with the pad. I haven't see where the cathodic protection is installed, if at all on this pad (outdoor pad), but if it is being used there, I can't see how it would work if there's no return path to earth.
Can someone enlighten me?