K8MHZ
- Electrician
Many years ago, like 15, I purchased 3 Woods brand remote control receptacle controllers. One of them started acting up, so you would have to have the remote a couple feet away from the controller in order to make it work. Yesterday, it failed altogether. So I decided to do an autopsy.
The first thing I noticed was that the controller was warm, and not even on. Just plugged in. Removing the cover revealed this:
Here is are some close ups of the burnt resistor: (Sorry, no macro lens....)
So, I decided to check the other controllers. They still were in working order.
Like the first one, the controllers were warm, and not on. Here is a pic of what they look like on the inside:
Just starting to burn.
Needless to say, I removed them from service.
All it says on the controllers is Woods No. 2023
I would have never thought that these things would be a heat source when plugged in and not in use.
That bites, too. I really liked the things, but now I can't really trust them. I wonder of the other brands are the same way?
If you own any of these, you may want to take a look at them.