I got a call over the weekend that some of my guys had tripped the Main Breaker in a newer building. I am getting all this second hand so bear with me. I want to get some ideas before i show up on Monday.
Here is what i know. This building is about 2 years old and is now finally getting built out for tenants. Some of the areas are already occupied. It has a very basic 3000 amp GE 480/277 gear. On one of the floors they have just finished installing about 30-40 lights. They went to energize the circuit and everything went down.
The gear has multiple 400 amp feeders that feed distribution panels on each floor. These panels on each floor then feed 100 amp panels that are for the 277 volt lighting. They energized one 20 amp circuit and the Main in the Gear opened. The 20 amp, 100 amp, nor the 400 amp did NOT trip. Only the 3000 amp Main tripped.
This job has engineered drawings with selective coordination done. The Ground Fault Protection in the gear has been tested and "SHOULD" have been set...?
The guys opened the 20 amp breaker and put everything as it was, then re-closed the Main. They did not investigate further.
Was this the GFP on the gear and could it be dialed down to low? I was screwing around to see what the Ground Fault current in the field would have been and i came up with this: Being supper conservative and only looking at the branch cirucit from the 20 amp breaker out to the "Fault" at or near a light would be about 200' (Gear, Main Panel, and lighting panel are only about 20' away from each other).
(200') #10 awg copper about (total resistance) 0.19978 ohms @ 277 Vac = 277/0.19978 = 1389 amps
Did the GFP see a fault of this magitude and open? One person did say they heard a hum and the lights stayed on for about 1-2 seconds.
Here is what i know. This building is about 2 years old and is now finally getting built out for tenants. Some of the areas are already occupied. It has a very basic 3000 amp GE 480/277 gear. On one of the floors they have just finished installing about 30-40 lights. They went to energize the circuit and everything went down.
The gear has multiple 400 amp feeders that feed distribution panels on each floor. These panels on each floor then feed 100 amp panels that are for the 277 volt lighting. They energized one 20 amp circuit and the Main in the Gear opened. The 20 amp, 100 amp, nor the 400 amp did NOT trip. Only the 3000 amp Main tripped.
This job has engineered drawings with selective coordination done. The Ground Fault Protection in the gear has been tested and "SHOULD" have been set...?
The guys opened the 20 amp breaker and put everything as it was, then re-closed the Main. They did not investigate further.
Was this the GFP on the gear and could it be dialed down to low? I was screwing around to see what the Ground Fault current in the field would have been and i came up with this: Being supper conservative and only looking at the branch cirucit from the 20 amp breaker out to the "Fault" at or near a light would be about 200' (Gear, Main Panel, and lighting panel are only about 20' away from each other).
(200') #10 awg copper about (total resistance) 0.19978 ohms @ 277 Vac = 277/0.19978 = 1389 amps
Did the GFP see a fault of this magitude and open? One person did say they heard a hum and the lights stayed on for about 1-2 seconds.