A new 1000 KVA step-up (208 -> 480/277) (220 deg C insul sys & 150 deg C rise) dry type power transformer was installed about 2 months ago to feed an existing 1600A busway.
Fused Switches on primary and secondary
Primary - 4000 A fuses
Secondary - 1600A fuses
It is located in a switchgear room which has a low ceiling (~7'). (More ventilation would help).
The primary cables B phase (10 sets of 3-600MCM THHN/THWN-2) are heating up to about 73 deg C (taken with thermal camera).
A and C phase are about 63 deg C (expected b/c B phase cables are directly above transformer coils).
Secondary cables are all much cooler (50 deg C) but are located in the back of the transformer (further from coils).
Spot load measurements taken
Primary - ~1800A
Secondary - ~830A
There is also a slight smell of burning insulation and the cover of the transformer is too hot to keep your hand on for more than a couple seconds.
Does the smell have anything to do with the transformer being brand new?
Are the 10 sets of wires at 73 deg C, a major concern? Are there any code requirements for wires to be rated above the typical 90 deg C?
p.s - first post, really enjoying the site.
Thanks
Fused Switches on primary and secondary
Primary - 4000 A fuses
Secondary - 1600A fuses
It is located in a switchgear room which has a low ceiling (~7'). (More ventilation would help).
The primary cables B phase (10 sets of 3-600MCM THHN/THWN-2) are heating up to about 73 deg C (taken with thermal camera).
A and C phase are about 63 deg C (expected b/c B phase cables are directly above transformer coils).
Secondary cables are all much cooler (50 deg C) but are located in the back of the transformer (further from coils).
Spot load measurements taken
Primary - ~1800A
Secondary - ~830A
There is also a slight smell of burning insulation and the cover of the transformer is too hot to keep your hand on for more than a couple seconds.
Does the smell have anything to do with the transformer being brand new?
Are the 10 sets of wires at 73 deg C, a major concern? Are there any code requirements for wires to be rated above the typical 90 deg C?