Forum,
We have an 800A feeder breaker in our plant that feeds two 200hp motors, each with a soft start. Each soft start has it's own upstream thermal-magnetic breaker. We tried starting one of the motors up one day and the feeder breaker tripped on Instantaneous, showing 4800 amps on all three phases (INST trip setpoint is 4800). From my understanding that indicates a three-phase fault. Technically if the coordination was correct, the thermal magnetic breaker for this motor should have tripped first, but I think the electronic trip unit on the feeder breaker is just too fast for the fault to trip the thermal mag. We looked at the wiring going to one of the motors and it looked pretty bad - scorch marks and such, so we think we found that culprit. We threw the thermal mag for that motor down and locked it out.
The really interesting thing - we wanted to start the other motor today, but when we immediately threw the thermal mag breaker up, it turned on the motor completely bypassing the soft start. We're pretty convinced that the SCRs are shorted in the soft start. My question is could the three-phase fault on the other branch cause damage to the soft start on this side? My thinking is it's all connected to the same feeder breaker, so would the other soft start see high amounts of fault current as well as the branch in which the three-phase fault occurred? Obviously if the breaker was down then no, but if it was up could it damaged the other soft start? Let me know what you're thoughts are on this.
We have an 800A feeder breaker in our plant that feeds two 200hp motors, each with a soft start. Each soft start has it's own upstream thermal-magnetic breaker. We tried starting one of the motors up one day and the feeder breaker tripped on Instantaneous, showing 4800 amps on all three phases (INST trip setpoint is 4800). From my understanding that indicates a three-phase fault. Technically if the coordination was correct, the thermal magnetic breaker for this motor should have tripped first, but I think the electronic trip unit on the feeder breaker is just too fast for the fault to trip the thermal mag. We looked at the wiring going to one of the motors and it looked pretty bad - scorch marks and such, so we think we found that culprit. We threw the thermal mag for that motor down and locked it out.
The really interesting thing - we wanted to start the other motor today, but when we immediately threw the thermal mag breaker up, it turned on the motor completely bypassing the soft start. We're pretty convinced that the SCRs are shorted in the soft start. My question is could the three-phase fault on the other branch cause damage to the soft start on this side? My thinking is it's all connected to the same feeder breaker, so would the other soft start see high amounts of fault current as well as the branch in which the three-phase fault occurred? Obviously if the breaker was down then no, but if it was up could it damaged the other soft start? Let me know what you're thoughts are on this.
Attachments
Last edited: