I have a situation where there is a 120/208Volt 3 Phase 600 Amp safety switch with double lugs (which is the max that is manufactured for a 600 Amp. per the manufacture) which is going to a 600 Amp. MDP, which also only comes with Double lugs. However the designer had planned on paralleling (3) 3/0 CU. and had installed (already installed under concrete) (3) runs of 2 1/2" PVC however with the situation of double lug max it will be difficult to run (3) conductors and will need to run a (2) wire system and that is with 350 MCM CU. and that runs into a problem of conduit fill. 2 1/2" PVC conduit only allows (4) 350 MCM and that doesn't account for the ground. Any suggestions would be appreciated.
Tx Gaylen