I'm installing a circuit to feed a car lift in a commercial garage and the nameplate rating is single phase 208 volt at 17 amps. Since the motor is over 80% of a twenty amp breaker, I'm wondering if there is a section of the NEC that would still allow me to put the lift motor on a 20 amp breaker. It's just the one motor on the lift with no other electrical components. I skimmed through article 430 but didn't see anything that applies to my situation
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
You may need to/be able to use a 30a breaker and use #12 cu wire.

Motors have high starting current, and a lift will likely be jogged often.

It sounds lie you want to avoid a larger breaker, or is it larger wire?
 

Little Bill

Moderator
Staff member
Location
Tennessee NEC:2017
Occupation
Semi-Retired Electrician
I'm installing a circuit to feed a car lift in a commercial garage and the nameplate rating is single phase 208 volt at 17 amps. Since the motor is over 80% of a twenty amp breaker, I'm wondering if there is a section of the NEC that would still allow me to put the lift motor on a 20 amp breaker. It's just the one motor on the lift with no other electrical components. I skimmed through article 430 but didn't see anything that applies to my situation
What does 80% of a 20A have to do with anything?
 

slc410

Electrician
Location
Madison wi
Occupation
Electrician
Not allowed to exceed 80% of the breaker I know is for continuous duty, but I'd like to find the code article where is says something along the lines of I can go over the 16 amps for a motor load. Is that better?
 

Little Bill

Moderator
Staff member
Location
Tennessee NEC:2017
Occupation
Semi-Retired Electrician
Not allowed to exceed 80% of the breaker I know is for continuous duty, but I'd like to find the code article where is says something along the lines of I can go over the 16 amps for a motor load. Is that better?
Only rule for that is, like you said, continuous duty. There is a 80% rule for receptacles, but nothing for breakers with a hardwired circuit other than what was stated.
You won't find a rule that says you are allowed. Code is a permissive code unless it says it's not allowed. They couldn't possibly say "allowed" for everything that is allowed.

16A x 125% = 20A
So you aren't going over anyway.
 

slc410

Electrician
Location
Madison wi
Occupation
Electrician
Only rule for that is, like you said, continuous duty. There is a 80% rule for receptacles, but nothing for breakers with a hardwired circuit other than what was stated.
You won't find a rule that says you are allowed. Code is a permissive code unless it says it's not allowed. They couldn't possibly say "allowed" for everything that is allowed.

16A x 125% = 20A
So you aren't going over anyway.
At the 17 amps on the nameplate it would be over 80% but I think I'm in the clear with no continuous duty load. Thank you for your help!
 