electrofelon
Senior Member
- Location
- Cherry Valley NY, Seattle, WA
So I took my Major load calcs portion of my Washington administrators on sat and got all 10 questions correct, but two of the questions I was a little unsure on and the numbers didnt match perfectly.
The first question asked to calculate using the alternative method the service load for a residential duplex. Now 220.82 applies to one dwelling unit and 220.84 applies to three or more, so what is the correct way to calc this? Only thing I could think of was to use 220.82 for each unit and add them together, was that likely the intended solution or did I miss something?
The other one was a bear, an industrial/commerical building with two occupants each having a whole bunch of stuff, calculate the service load. Okay so I dont remember the exact loads and even if I did I think I agreed to not release, discuss, share any details of the questions..but to see if I was on the right track and just made a minor math error, some questions:
1. For calculating the service, I can essentially lump all the stuff in both units together right? How many units there are doesnt really effect any demand factors or anything other than each one needs 1200VA for a sign, correct?
2. There were a bunch of motors. I take the 125% of the largest one using table 430.24x and add the 430.24x value of all the other ones, correct?
3. Heat was larger than AC so I just use 100% of the heat Nameplates, correct? If Ac was larger than heat do I use 100% or 125% of the AC nameplate?
4. I did 2 VA per square foot for gen lighting, 100% demand.
5. Each of the two units had a large fridge and a microwave. I add the nameplate of those four together and get to use 80% demand from 220.56.
I think thats it, there was some show window and a bunch of receptacle outlets but I dont think i could have screwed that up. I used the demand factors 220.44 for non dwelling unit receptacles.
Thanks
The first question asked to calculate using the alternative method the service load for a residential duplex. Now 220.82 applies to one dwelling unit and 220.84 applies to three or more, so what is the correct way to calc this? Only thing I could think of was to use 220.82 for each unit and add them together, was that likely the intended solution or did I miss something?
The other one was a bear, an industrial/commerical building with two occupants each having a whole bunch of stuff, calculate the service load. Okay so I dont remember the exact loads and even if I did I think I agreed to not release, discuss, share any details of the questions..but to see if I was on the right track and just made a minor math error, some questions:
1. For calculating the service, I can essentially lump all the stuff in both units together right? How many units there are doesnt really effect any demand factors or anything other than each one needs 1200VA for a sign, correct?
2. There were a bunch of motors. I take the 125% of the largest one using table 430.24x and add the 430.24x value of all the other ones, correct?
3. Heat was larger than AC so I just use 100% of the heat Nameplates, correct? If Ac was larger than heat do I use 100% or 125% of the AC nameplate?
4. I did 2 VA per square foot for gen lighting, 100% demand.
5. Each of the two units had a large fridge and a microwave. I add the nameplate of those four together and get to use 80% demand from 220.56.
I think thats it, there was some show window and a bunch of receptacle outlets but I dont think i could have screwed that up. I used the demand factors 220.44 for non dwelling unit receptacles.
Thanks