bobby ocampo
George Stolz said:Grounding Vs. Bonding
The Big PictureGrounding and bonding is probably the most discussed issue here, aside from 210.52?s design requirements.
- What is ?grounding?? What is ?bonding?? What?s the difference?
The terms are defined in Article 100 and 250.2 of the NEC. Section 250.4 provides the performance requirements of Article 250. Grounding is a connection to earth, and bonding is the connection of items to each other.
Bonding is crucial inside a structure, because without it, if something goes wrong and an ungrounded conductor comes in contact with a piece of metal that someone can touch, that someone will receive a shock and potentially be electrocuted due to the uncleared fault. A quick and dirty definition for bonding is connecting electrical devices together in the attempt to trip a breaker, if an ungrounded conductor touches surface metal associated with the system.
This is true only SOLIDLY GROUNDED SYSTEM because of a very high current on a single line-to-ground fault but not on UNGROUNDED system and HIGH RESISTANCE GROUNDED SYSTEM. Single line-to-ground fault for UNGROUNDED SYSTEM and HIGH RESISTANCE GROUNDED SYSTEM is very small. A person will receive a shock if the piece of metal is not connected to earth but not because of an uncleared fault.
George Stolz said:What does the earth have to do with this? Nothing.
Earth has something to do with safety to reduce the potential of the energized piece of metal to zero potential or ground potential. Justification can be seen in an UNGROUNDED SYSTEM or HIGH RESISTANCE GROUNDED SYSTEM.
George Stolz said:Then why is it called an ?Equipment Grounding Conductor (EGC)? in the NEC if it?s primary purpose is to ?bond? things together? Simple answer: tradition. It?s always been called that, and the terms in the NEC have served to confuse people for a long time. Proposals have been made to change the term, and progress has been made, but the EGC continues to hold it?s misnomer.
I respectfully disagree sir. Vector diagram will show specially in a high resistance grounded system, that if an ungrounded conductor touches the ground its potential will be reduced to ground potential. This can be verified in an experiment both for UNGROUNDED SYSTEM and HRG system.
George Stolz said:Electricity does not seek the path of least resistance to the earth. It seeks all available paths back to it?s source, in proportion to their resistance. The reason that a person gets shocked when touching an ungrounded conductor and the earth is because the neutral of the system is repeatedly connected to earth in a grounded electrical system. The earth becomes part of a return path to the transformer ? it?s part of one route back to the source; the earth is not the destination for the electricity.
Sir, Even if the neutral is not grounded to earth a person touching an ungrounded condutor will be electrocuted because of the system capacitance. Reference' Industrial Power systems handbook by Beeman.
George Stolz said:Driving a ground rod to ?ground? any electrical equipment does not provide the low-resistance path required to trip breakers. Driving a ground rod, or using a Ufer, or a metal water pipe is not a substitute for an EGC. A ground rod with 25 ohms to earth will allow almost five amps to escape the system into the earth when directly energized from a 120V source. Five amps will never trip a 15A or 20A breaker, and in the meantime everything bonded to this ground rod will be energized to 120V.
The purpose of the ground rod is not to provide low resistance path but to make all equipment equipotential to the ground for safety. This can be proven by experiment on UNGROUNDED SYSTEM and HRG system.