ches2443
Member
- Location
- deal island, maryland
I feel that the ground rod was misnamed; it should of been called the bond rod. (In a nutshell) Bonding is to equalize two unequal potentials. Grounding is for tripping breakers during ground faults.
ches2443 said:I feel that the ground rod was misnamed; it should of been called the bond rod. (In a nutshell) Bonding is to equalize two unequal potentials. Grounding is for tripping breakers during ground faults.
ches2443 said:Sorry I spoke out of turn.
Here,here!! I couldn't agree more. These terms would lead to so much less confusion.iwire said:Can't agree there, if there is anything we are going to call 'ground' in the NEC it better be the item that actually connects to the earth.
IMO the term 'grounding' should be used exclusively for the items that make up the grounding electrode system.
What we presently call the equipment grounding conductor should be renamed the equipment bonding conductor.
CMP 5 didn't agree when I and two others submitted proposals to that effect for the 2005 code.iaov said:Here,here!! I couldn't agree more. These terms would lead to so much less confusion.
iwire said:Can't agree there, if there is anything we are going to call 'ground' in the NEC it better be the item that actually connects to the earth.
IMO the term 'grounding' should be used exclusively for the items that make up the grounding electrode system.
What we presently call the equipment grounding conductor should be renamed the equipment bonding conductor.
Electricity does not seek the path of least resistance to the earth. It seeks all available paths back to it?s source, in proportion to their resistance. The reason that a person gets shocked when touching an ungrounded conductor and the earth is because the neutral of the system is repeatedly connected to earth in a grounded electrical system. The earth becomes part of a return path to the transformer ? it?s part of one route back to the source; the earth is not the destination for the electricity.
Michael15956 said:I agree and in that opinion I set up an experiment in my shop to establish some evidence to this belief.
I wired a circuit with a switched light on a GFCI protected receptacle. Connected another switch in parallel downstream of the first switched light. With the first switch close, light lit, and the second switch open I connected a load on the ungrounded terminal on the load side of the second opened switch and the GFCI receptacle open every time.
My conclusion, was that the current on the ungrounded conductor was trying to seek all paths back to it's source and created an unbalanced condition in the GFCI receptacle and it opened the receptacle.
I think so. What do you think?dmanda24 said:Is the information in here still valid for the 2008 NEC
Care to elaborate? Proposal season is closing on us.weressl said:(I wonder why the US folks do not take a look at the IEC work on the issue that is much better defined in this case with earthing and protective earthing, etc. Not invented here syndrome?)
George Stolz said:What do you think?
Did they tell you a reason for rejecting the proposal?don_resqcapt19 said:CMP 5 didn't agree when I and two others submitted proposals to that effect for the 2005 code.
Yes..they said the change in terms would be too confusing and create a bigger problem than the one I was trying to solve.iaov said:Did they tell you a reason for rejecting the proposal?
don_resqcapt19 said:Yes..they said the change in terms would be too confusing and create a bigger problem than the one I was trying to solve.
iwire said:Pretty lame excuse IMO.