I'm replacing a feeder at a local school, 400 amp, 120/208y, 500' long. This school has a main service freestanding in the middle of campus, with 4-5 separate buildings fed from there.
The contractor that pulled the particular feeder we're replacing did not pull an EGC, but bonded the neutral at both the main service and the building service. Perfectly acceptable, but not the best method , especially in a school imo.
I emailed the district admin and his electician today explaining why I wanted to pull an EGC and why we need to add a ground buss to the building's service and isolate all the building's EGCs from the neutral buss.
Obviously with the neut being used as the EGC there's the potential for parallel paths, which got me thinking.
How many possible paths could exist?
The obvious possibilities:
water service
nat. gas
circuits common to multiple buildings (house lights, ect.)
not so obvious:
cast iron plumbing?
grounded phone, alarm, signaling, ect. conductors common to two or more buildings?
Maybe none, maybe several.
Am I right for asking to install an EGC? When no obvious metal paths connect the building to other buildings fed from the service or the service itself isn't it prudent to assume these paths could exist in many forms?
The contractor that pulled the particular feeder we're replacing did not pull an EGC, but bonded the neutral at both the main service and the building service. Perfectly acceptable, but not the best method , especially in a school imo.
I emailed the district admin and his electician today explaining why I wanted to pull an EGC and why we need to add a ground buss to the building's service and isolate all the building's EGCs from the neutral buss.
Obviously with the neut being used as the EGC there's the potential for parallel paths, which got me thinking.
How many possible paths could exist?
The obvious possibilities:
water service
nat. gas
circuits common to multiple buildings (house lights, ect.)
not so obvious:
cast iron plumbing?
grounded phone, alarm, signaling, ect. conductors common to two or more buildings?
Maybe none, maybe several.
Am I right for asking to install an EGC? When no obvious metal paths connect the building to other buildings fed from the service or the service itself isn't it prudent to assume these paths could exist in many forms?