A fellow inspector has recently found some of these panels mis-wired, as shown. Unsure why the manufacturer (GE) has the double lugs but it lends itself to a serious connection mistake
View attachment 20530
+1I think the double lugs are so you can come in and then feed out. Not the manufacturers fault that some nitwit did not read the instructions first.
As it is now, it looks as though there is no bonding jumper in place.
JAP>
It also looks like the GEC is connected to the EG bus instead of the neutral bus. But, based on the dead short on the ungrounded conductors the improper grounding and bonding may be the least of their problems.
On a side note, I hate those 30 amp 125v Rv receptacles.
The screws are both brass making it a document search to assure yourself of the hot and the neutral side to land your wiring on.
JAP>
If you purchase as part of an assembly like in the OP - it is already connected for youOn a side note, I hate those 30 amp 125v Rv receptacles.
The screws are both brass making it a document search to assure yourself of the hot and the neutral side to land your wiring on.
JAP>
Unless this is service equipment it shouldn't be connected to the neutral bus.It also looks like the GEC is connected to the EG bus instead of the neutral bus. But, based on the dead short on the ungrounded conductors the improper grounding and bonding may be the least of their problems.
If you purchase as part of an assembly like in the OP - it is already connected for you
Not on a 30 amp power outlet only it's not.
Unless this is service equipment it shouldn't be connected to the neutral bus.
At times I find this place a little unbelievable.
The intent of the original post happened not to be "what all is wrong with this picture". It meant to be a precaution to folks that there is the possibility of making a serious connection mistake if you run across one of these panels and are accustomed to single lug panels.