When a metallic enclosure or raceway is effectively grounded, it will have _________ potential with respect to ground.
 
Re: potential to ground

That is a very poor question. There is no way to correctly answer it. The voltage to "earth" changes with the conditions. For example under a fault condition the raceway will have a voltage to earth approximately equal to the voltage drop on the grounded conductor between the power source and the main bonding jumper.
Don
 
Re: potential to ground

Test time? You'll get zero answers here.
Clue!!!, find out what potential means, and you have your answer.
 