potential

Status
Not open for further replies.

bond

Member
is there such a thing as a potential between the neutral and the ground?(water pipe,ground rods)Is there a balance thats needed between these two(ground and grounded)in order for the service to opperate effectively.Im told that if i had no ground at all either to the ground rod or water pipe the system will act funny.Is this true? is it important or not,why all the debate?havent we figured this out already? thanks
 
Re: potential

Originally posted by bond:
is there such a thing as a potential between the neutral and the ground?(water pipe,ground rods)
Yes

Is there a balance thats needed between these two(ground and grounded)in order for the service to operate effectively.
No, the service will operate just fine with no connection to the earth.

I'm told that if i had no ground at all either to the ground rod or water pipe the system will act funny.Is this true?
I do not know what you mean by funny.

In my opinion the primary reason for connecting the neutral to the earth is protection of the premises wiring from lightning or high voltage imposed on it from a power company fault.
 