I have 800 amp services on the end of each building. each with 18 meters 1ph 120/208 125a-
one with an additional house meter, 3ph 4w 120/208 225. I noticed in the house panel and in the 125 amp 1ph panel, i’d have straight continuity between the neutral and ground, as I should. Once I turn on the lighting circuits the the continuity on my meters sounds like it comes and goes, like something is disrupting it or it’s loose. Comes back when lighting is turned off again. Continuity between neutral and ground at the service remains even while everything is energized, unlike the panel. my feeder connections are tight and neutral bonded in the main cabinet. From each service I have a UFER ground and a 3/0 copper to 4” underground water pipe.
one with an additional house meter, 3ph 4w 120/208 225. I noticed in the house panel and in the 125 amp 1ph panel, i’d have straight continuity between the neutral and ground, as I should. Once I turn on the lighting circuits the the continuity on my meters sounds like it comes and goes, like something is disrupting it or it’s loose. Comes back when lighting is turned off again. Continuity between neutral and ground at the service remains even while everything is energized, unlike the panel. my feeder connections are tight and neutral bonded in the main cabinet. From each service I have a UFER ground and a 3/0 copper to 4” underground water pipe.