I recently had an electrical contractor through who installed a new QO panel. Due to the antiquated nature of the main panel feeding the new panel, the OCPD is a 100 amp E-frame Westinghouse unit, and I cannot see any temp rating on the unit.
As I understand it, if no temp rating is evident, the conductor gauge must be specified from the 60deg column of table 310.16. He installed a #1 aluminum conductor, which is only good for 85amps at 60deg C, and as such is undersized for the application.
Before I politely ask about his choice of conductor here, I wanted to ask if anyone had any experience with the old Westinghouse OCPD's and if there was any potential that they were good to 75deg C?
Best,
As I understand it, if no temp rating is evident, the conductor gauge must be specified from the 60deg column of table 310.16. He installed a #1 aluminum conductor, which is only good for 85amps at 60deg C, and as such is undersized for the application.
Before I politely ask about his choice of conductor here, I wanted to ask if anyone had any experience with the old Westinghouse OCPD's and if there was any potential that they were good to 75deg C?