Classification for area around actual powder coating booth. Area is used for storage of excess powder for the process.
Thanks
Thanks
Classification for area around actual powder coating booth. Area is used for storage of excess powder for the process.
Thanks
Depending on the actual material is could be a dust under Articles 502 and 516. The primary applicable classification Standards are NFPA 34 and 499. Both are referenced in Section 500.4(B) Informational Note No. 2. As usual, it takes understanding the process and geometry of the installation.Is a powder coating booth typically classified? I have seen several and I don't recall they looked like there was anything special going on.
But if it is classified it is likely Class II and the requirements there are not as obvious as Class I.
You are aware that NFPA 484 says nothing about classifying hazardous locations in the sense of Articles 500, 502, and 516 and is useless with regard to the original post, right? In fact you don't even know the coating material is metallic.NFPA 484
Standard for Combustible Metals-metal alloys are subjected to processing or finishing operations that produce combustible powder or dust.
This standard applies to the production, processing, finishing, handling, recycling, storage, and use of all metals and alloys that are in a form that is capable of combustion or explosion.
Of course if it is sugar dust - Sugar-land Texas & explosions can give you a great deal of information based on operation of horizontal conveyors, motors , bearing temperatures on and on.
You may wish to read the Scope of Article 516.:So I guess in all fairness I gravitated to your suggestion dust is what the original post intended evn though he did not ask taht question his question was about powder.
Since powder does not appear to be a term NFPA 70 NEC articles why are you allowed to make the ruling your post has any validity what so ever?
The framers of thew forum charter rules discourage offering assistance with non compliant NEC terms and definitions and article 500 specifically disclaims any evaluations "This code does not classify areas where explosive materials such as , dynamite and blasting powder are present." NFPA 70 code under 500.1 Scope"... only limited locations classified as Class I, Class II, Class III , which are further addressed in Articles 501,502 and 503."
It appears reading for comprehension is not you strong suit. Your reference to NFPA 484 still doesn't apply to the original post (OP) and my initial response didn't say the material was a dust, simply that it could be and Articles 502 and 516 would apply and the appropriate classification Standards are NFPA 34 and 499.516.1 Scope. This article covers the regular or frequent
application of flammable liquids, combustible liquids, and
combustible powders by spray operations and the application
of flammable liquids, or combustible liquids at temperatures
above their flashpoint, by dipping, coating, printing,
or other means.