I have an equipment spec that's listed as the following:
Voltage = 220
Single Phase
Frequency = 60Hz
Current = 20A
Power = 4000W
That said, if I assume the p.f. to be 1.0, the VA should be the same as the power, which is 4kVA, correct?
If I'm using a 120/208Y, 3 phase, 4 wire panel, the 220V spec indicates I should be using a double-pole breaker, correct?
Also, let's say it is a double-pole breaker for this equipment and I put it across A & B phase, does each phase read 2kVA (assuming my first question is correct, I divided 4000VA by 2), or does each phase read 4kVA? What about if it was a 3-pole breaker?
Thanks!