tkb Senior Member Location MA Apr 5, 2017 #1 Can you install 480v conductors and fiber optic cable in the same raceway? Does 300.8 apply? I would consider FO as an electrical system since it is in 770. 770.110(B) refers to FO and power in the same raceway. Seems okay to me. What do you think?
Can you install 480v conductors and fiber optic cable in the same raceway? Does 300.8 apply? I would consider FO as an electrical system since it is in 770. 770.110(B) refers to FO and power in the same raceway. Seems okay to me. What do you think?
M Mouser Member Location Riverside, CA. Apr 5, 2017 #2 I think 770.133 is what your looking for as long as the FO cable is nonconductive.