Are there any issues, interference if power and telecom conduits (has low voltage data wires) run side by side, probably 3"-6" apart?
 
In metallic conduits, none. In non-metallic conduits, little.

Modern data lines are almost immune to 60 Hz interference.
 
National Electric Safety Code [C2-2007] Rule 320 Location B. Separation from other underground installations
 

Attachments

  • NESC C2 2007 Rule 320 B 2.jpg
    NESC C2 2007 Rule 320 B 2.jpg
    19.5 KB · Views: 19
In metallic conduits, none. In non-metallic conduits, little.

Modern data lines are almost immune to 60 Hz interference.
For 60Hz and modern, in the sense of Ethernet, they should be close completely immune. A voltage induced on D+ will also be induced on D-, and the difference will remain constant. If there is going to be a problem it will be on non-differential lines, like RS-232, and not differential lines, like Ethernet, RS-485, RS-422, etc.

In the OP's case, the question should be if this is VoIP or regular telco.
 