I understand that most LV Power Circuit breakers have two ratings which are the interrupting rating, and the withstand rating. For most breakers it is my understanding that the interrupting rating is based off of a 1/2 cycle timeframe while the withstand rating is based off of a 30 cycle timeframe, is this correct?
I was looking at a particular breaker that had a 65kA interrupting rating but only a 10kA withstand or short time rating. I guess my question is when do we need to be concerned with the withstand rating and how it compares to the avaliable fault curent at the given location. Usually for equpment evaluation the lowest device interrupting rating in the equipment is compared to the avalaible fault current to determine the pass/fail of the equipment evaluation. When do we need to check to ensure tha the breakers withstand rating meets the necessary requirements.
The only case I can think of is if the given power breaker is located in the panel and has its instantanous seeting turned off, then the withstand rating has to meet the fault current rating? Or does it depent on what is upstream of the breaker or panel?
I was looking at a particular breaker that had a 65kA interrupting rating but only a 10kA withstand or short time rating. I guess my question is when do we need to be concerned with the withstand rating and how it compares to the avaliable fault curent at the given location. Usually for equpment evaluation the lowest device interrupting rating in the equipment is compared to the avalaible fault current to determine the pass/fail of the equipment evaluation. When do we need to check to ensure tha the breakers withstand rating meets the necessary requirements.
The only case I can think of is if the given power breaker is located in the panel and has its instantanous seeting turned off, then the withstand rating has to meet the fault current rating? Or does it depent on what is upstream of the breaker or panel?