Power cable in cable tray

Status
Not open for further replies.

StanSmith

Member
hello all;

Is it ok to have power cables, that go to 480VAC power distribution panels, inside a cable tray ? I haven't seen anything in the NEC against that...

Regards,
Stan
 

Smart $

Esteemed Member
Location
Ohio
hello all;

Is it ok to have power cables, that go to 480VAC power distribution panels, inside a cable tray ? I haven't seen anything in the NEC against that...

Regards,
Stan
It is OK. Have personally experienced up to 13.8kV cable installations in tray. Not much else I can say :D
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
hello all;

Is it ok to have power cables, that go to 480VAC power distribution panels, inside a cable tray ? I haven't seen anything in the NEC against that...

Regards,
Stan

There is nothing wrong with running 480V cables in cable tray. Is this a ladder type tray?

Are there other conductors in the same tray?
 